One thing I do want to point out, is that the PID loop isn't set up inside the VFD, but rather in our PLC.
doesn't matter as long as tuned well
a plc gives alot more flexibility
One thing I do want to point out, is that the PID loop isn't set up inside the VFD, but rather in our PLC.
Might as well. V/Hz control is just the basics of what a VFD can do. From there you get into various forms of "Vector Control" that improve torque control and response to changes in loads, but on a centrifugal pump that does little to nothing to enhance your experience. The down side however is that for Vector Control to function, it must be "tuned" to the motor. That's not too difficult either now days, but if you ever someday have to replace the motor, that means the drive must be tuned again to the new motor. If there is nobody available who knows how to do that when it happens (because Murphy's Law says it will happen at 3:00AM on Christmas Eve), then your pump is down until that person is available. Using V/Hz means that issue is not there, so any time the motor is swapped, the drive doesn't care. I always recommend using V/Hz on centrifugal loads for that reason alone.just got word this is a centrifugal pump, is V/Hz still recommended?
doesn't matter muchjust got word this is a centrifugal pump (so variable torque), is V/Hz still recommended?
Just for the record, not ALL pumps that are not positive displacement are necessarily centrifugal. Axial flow (propeller) and "mixed flow" pumps started into a filled system can display a mixture of CT and VT characteristics depending on the speed and head conditions, so the drives should often be sized as CT to be safe. But yours is a vertical turbine pump, so VT sizing should be fine.
You will find that most (if not all) motor mfrs will tell you that if a motor is run from a VFD, the SF becomes 1.0.keep in mind many pumps have a sf >1.15 so you may want to set ol's higher, ie, heavy duty
You will find that most (if not all) motor mfrs will tell you that if a motor is run from a VFD, the SF becomes 1.0.
At 300HP, the cost difference is significant, I likely would have gone ahead with ND, but there is nothing wrong with HD if you can afford it.Since this was my first foray into VFD's larger than 30hp, I went ahead and sized it for a Heavy Duty rating of 300 hp, Normal Duty rating of 350 hp, just to err on the side of caution.
Is it generally safe to say that if the load is constant torque, then size VFD according to Heavy Duty rating, and if the load is variable torque, then sizing according to Normal Duty rating is acceptable?
Makes sense. Many just throw a drive on an existing application for various reasons and never consider if the motor might already been running into any service factor load levels.
I can't say I have seen a lot drawing more then FLA on nameplate, but seems they are seldom drawing less then ~90-95% of FLA. They want to get every bit of HP out of them it seems. If you have a need for 85 HP then they go ahead and change sprinkler package to get closer to 100 since they are buying a 100 HP motor anyway.I don’t remember an irrigation motor that isn’t running SFA.
Since this was my first foray into VFD's larger than 30hp, I went ahead and sized it for a Heavy Duty rating of 300 hp, Normal Duty rating of 350 hp, just to err on the side of caution.
Is it generally safe to say that if the load is constant torque, then size VFD according to Heavy Duty rating, and if the load is variable torque, then sizing according to Normal Duty rating is acceptable?
If you go with heavy duty rated VFD, please consider that 430.122(A) requires circuit conductors be sized not less than 125% of the rated input current to the VFD. If you are reconnecting existing conductors they might not have adequate capacity.
Is the motor inverter duty rated? My guess would be no since it was originally across-the-line. The motor might not be compatible with a VFD without other considerations.
More of a problem in vertical pumps as opposed to horizontal, the VFD exposes the parts inside the motor to high-frequency currents which travel to ground through the shaft and bearings. This causes pitting leading to premature failure. One solution involves installing an alternative path to ground for the stray currents. There is a lot of information floating out there, good and bad, in regards to this topic, and I do not consider myself an expert.
Please consider a dv/dt output filter if the distance from the VFD to motor is longer than a couple hundred feet. Even better, discuss with VFD manufacturer and they can tell you if dv/dt is recommended.
You might benefit from having a conversation with the motor manufacturer and pump manufacturer and explain to them what you are doing. Express a concern regarding premature bearing failure due to VFD. They might offer some insights or recommendations.
what percent of the total load served by the xfmr that serves the vfd/pump is the vfd/pump?
what size xfmr?
This 300 hp pump is by far the largest motor served by this transformer, I'd say it's 80 percent if not higher of the total load. The transformer is 2500kVA. The other remaining loads include small motors, a 480v panel, and some 120/240v panels. I did include line reactors in the design.