That is somewhat a loaded question. With a variable torque driven load, current will generally be lower at lower speed.
Constant torque load which applies to your conveyor - current can be same at low speeds as it is at high speeds, this really depends on the driven load characteristics. For simplicity lets say the motor draws 10 amps at 60 hertz when fully loaded. Now change frequency to 30 hertz and you have half speed, if current remains at 10 amps and voltage remains at same volts/hertz ratio, your output power is half what it is at full speed. That is a truly contestant torque situation there..
replacing a 4 pole motor with a 2 pole motor of same HP and driving same load - the two pole motor should draw more, but is doing about 2 times the work because it is running at 2 times the speed. Place gearbox, pulleys in the mix to get same final output speed and the current should be similar, but will vary based on efficiency and power factor differences in the motors themselves along with any losses in the speed reduction method.