here's the issue based on what we know
valve drop ~40 psi, 100 ft hd, valve appears full open
hp = 40
meeting demand
if we slow the pump down we loose head and pressure
the valve can't open more
if you remove the valve you need to add controls
let's say we reduce pressure to 60/96 ~ 7 psi across valve
pressure is 60% of original
flow drops to 40% of original
demand not met
P = 0.6^^1.5 x 40 =19 hp
speed ~ flow ~ 60 x cubert(0.4)= 43 Hz
but pump eff will drop, so hp req may be like 0.7/0.6 x 19 ~ 23 hp or more
still only need less than 10 hp
get a pump sized for current flow at 60 psi, set prv ~ 50-55
I would do a real analysis before doing anything
you might make things worse