kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
But you are trying to find a way to reduce conductor size so it will fit in your raceway.This quote applies as follows: Imagine you have a bunch of 20A circuits, which typically are run using 12ga wire, protected by a 12ga EGC. Say you had a bunch of 75C rated wire and had to run 9 'current carrying conductors' in a single conduit. Derating rules would push you up to 10ga wire and you would also be required to use a 10ga EGC. But if instead you used 90C wire you would be derating from a 30A ampacity and you could stick with 12ga wire.
Note however that the voltage drop in these hotter 12ga conductors would be greater than the same conductors operating at a lower temperature.
The quote is not saying that voltage drop is the same in conductors of the same ampacity but different temperature ratings, rather it is noting that you can use the higher temperature rating to reduce the conductor size for purpose of derating, and thus avoid having to increase the size of the EGC.
Reducing conductor size will always increase voltage drop.
-Jon
Yes higher temp insulated conductor will have more ampacity per the tables, but at same time will increase VD if you use that additional capacity. Same conductor will still have same VD characteristics regardless of what insulation is on it, all the higher temp rating does is allow higher insulation temp before compromising insulation integrity becomes a concern.
You are adding one benefit but taking another away. May not be 1:1 difference so details are important.