So the term "Adjusted load" what does that mean; am I being to literal in hoping that the demand load and the adjusted load are not the same?KP2
I did not mean taking 66% of the total bldg load.
I do this for the apartment feeder ONLY....meter stack to apartment.
If your adjusted load for the meter stack is 1083 amps you must use this for your calc.
The demand load is 1083 amps, which is the result of the feeder calculation based on 220.84.