I guess I have some splan'n to do.
Standard thermal magnetic breakers were going to meet the requirements of 210.12, until it was brought up that some new homes may have 500 amps at the panel-board due to long or undersized service drops- leading to 75 amps vs 200 amps of assumed fault current at the end of a typical 15 or 20 amp run.
Standard breakers with a 150 amp magnetic pickup will hold on inrush, where as 75 amps will cause a trip. Hence electronics were created to ironically hold on inrush over 75 amps, yet still be able to detect arcing short circuits down to 75 amps.
Between 1000 and 10,000 amps (0.12-0.012ohms) little difference is made on the short circuit current of a branch circuit at the far end, while fault currents under 1000 amps begin to cause a rapid drop in current magnitude.
Low current flow during a fault increases EGC heating and touch voltage, sometimes to the point where it can be in violation of code.