I’ve just put a similar supply in, single phase 25kVA over 4000Ft. The source was 433V stepped up to 3.3kV, a 25mm² 3c SWA cable and then stepped down to 240V. Volt drop at FLC 0.55%
The savings on cable and cable laying more than made up for the cost of the transformers.
25mm² = 2AWG
The savings on cable and cable laying more than made up for the cost of the transformers.