If a big voltage drop is outside the part of the circuit that you run at higher voltage you will not change that part of the totsl voltage drop.
If you look at just boosting the voltage at the load with a boost transformer or a tap change, you will still have the same swing between loaded and unloaded condition, the average and minimum voltages will just be higher.
For a motor load that might decrease the load current enough to slightly reduce the voltage drop in that part of the circuit only.
If you do not change the voltage on the feeder you will not change the voltage drop on the feeder.