kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
understandable, bet there was still significant heating and maybe even getting to point you wouldn't want to touch it. Temp needed to melt insulation is higher than you want to touch.Right, however notice the thicker primary conductors do not smoke let alone glow red.
Given about 40 seconds of opening time for a 60 amp breaker I'm guesstimating about 150 amps of fault current.
Don't know what size of the wire is, maybe 10 or 8 AWG - looking at title maybe 6mm? I think 6mm is between and 4 AWG though, it don't look that big to me.