May not lessen enough in some instances, but Ohm's law still applies. Current in a conductor is limited by resistance of the conductor. Increase conductor size and you lessen conductor resistance, maybe enough to allow OCPD operation in desirable time.
Voltage drop at "normal load" is one thing, voltage drop at fault current levels is going to be much more, though fault current will still be limited by impedance of the circuit.
And as I said before making a fuse link out of a short length of small conductor is not the same thing as having several hundred feet of same size conductor - the resistance of those several hundred feet is going to be current limiting and you will not get the same fault current. Depending on circumstances may still melt the conductor but won't be in the same amount of time. Good connections is important, a connection is likely to be what has complete failure first in this situation.