Other than that, I finally get it for an unbalanced linear system... but now thinking about how to apply that to my 2nd diagram seems like a nightmare, and even more so when I actually try to apply it to the plans I am looking at.
Then don't. Figure out a simplified balanced system that you can demonstrate will be worse than the unbalanced system. Then do the calculation for that simplified system know will give larger wire sizes than the perfect calculation. Use the larger wire size and just figure that the extra cost of copper is cheaper than the design time to figure out the exact wire sizes to use, and knowing that you will also be saving a smidge of electricity over the life of the project.
-Jon