So the engineer designed (2) sets of 1/0 from 300A breaker to the wiring trough but also added a note that VD must be kept below 2%. The norm is 3%. The run is 300' to the trough. At the 120/208 voltage I see it seems the 1/0's won't work at all. The Southwire VD calculator I'm using is asking current at end of run. Not exactly sure what to put at the (2) sets go to the trough then splice and go to a 60A panel and panel MDP which is 225A. For now I'm entering 300A current at end of run. It is giving me (2) sets of 500. Far off from the 1/0 the engineer is specifying. Would also have to upsize the conduit if my calculation is correct.
Ridiculous the engineer did not specify proper size.