No need to worry about the 75° C. Almost no equipment has 60° C terminations therefore the #6 tap conductor is good for 65 amps. You're correct that the 10' tap rule would apply to the #6's.
While true, the plans should it when the calculation makes the assumption that only 75°C rated equipment, wires, terminations, etc. will be purchased and installed.