Can you explain a little more about panel calcs being bloated? you mean the calculated load or panel rating or both? Shouldn't the calc load be fairly close to reality?Modern over engineering. The panel calculations are typically bloated and not highly accurate as far as the real world usage.
Most panel loads have some built in demand factors meaning that not every load in a panel will be running at the same time.Can you explain a little more about panel calcs being bloated? you mean the calculated load or panel rating or both? Shouldn't the calc load be fairly close to reality?
3 main things:Can you explain a little more about panel calcs being bloated? you mean the calculated load or panel rating or both? Shouldn't the calc load be fairly close to reality?
Not sure if you are seeing any of my posts, but as I said in post number two I would often assume 50 to 66% of NEC calc for the voltage drop calc.Ok thanks. Curious as to how others think I should approach this. I already priced the job with the 1/0's shown on the engineers drawings.
I did not take the drawing note about 2% into considerations. My bad. I did make them aware of this and will follow up with client tomorrow.
Is it as straight forward as saying the 1/0's( and conduit size) won't work because of the calculated load and having to keep VD to 2% or could I spin it a little and state that the calculated load is probably overblown and would really be a particular % less.....although we'd never really be able to determine that based on a calculation at this point?
Are you a gambler? If so install the #1/0's as per the drawing and keep you fingers crossed. The fact that the engineer came up with the #1/0's initially seems like this isn't your problem. It should have been the designers job to do the calculation not yours.Ok thanks. Curious as to how others think I should approach this. I already priced the job with the 1/0's shown on the engineers drawings.
Explain further. You mean 50-66% of which number?Not sure if you are seeing any of my posts, but as I said in post number two I would often assume 50 to 66% of NEC calc for the voltage drop calc.
The panel schedule in post #17 seems off.Would the calculated load of this panel be the total VA? If so I'm getting 227A.
Since this is a distribution panel I would guess that those 1Ø loads (1D, 1G, 1J, etc.) are sub-panels.Second, all the loads are shown as single pole. What kind of load is 11582 VA @ 120V? That's 96.5A.
CorrectSince this is a distribution panel I would guess that those 1Ø loads (1D, 1G, 1J, etc.) are sub-panels.
OK, good point, so a bunch of 120/208 3-wire subpanels supplied by this 208Y/120V 3-phase panel.Since this is a distribution panel I would guess that those 1Ø loads (1D, 1G, 1J, etc.) are sub-panels.
I agree likely another error.Still, the panel at location 1G is supplied by a 60A breaker, but the load on leg C is shown as 11582 VA, which is 97A @ 120V. That's a problem.
Since voltage drop is not an NEC requirement, I don't see that any justification is needed for whatever method or diversity Factor is used..
When I do voltage drop calculations I use the calculated load. I don't see anything in the NEC that allows a diversity factor for voltage drop calcs. I agree that actual load in commercial is typically 50% of the NEC calculation and actual load for residential is even less, but just because I know that does not mean I can use those factors.
No need to worry about the 75° C. Almost no equipment has 60° C terminations therefore the #6 tap conductor is good for 65 amps. You're correct that the 10' tap rule would apply to the #6's.This looks like the same plans from an earlier post with the tap. The EGCs are still sized incorrectly. #6 is 55A without a note for everything to be 75°C. Which would violate the tap rule.