Mike01 said:
In a square d catalog for busway systems it gives an example for 1000A 50% pf bus duct as follows:
Sqrt(3) * I (R cos? + X sin?)
Sqrt(3) * 1000 (.00163 *.5 + 0.00093 * .866)
What I do not understand is where are the numbers in bold derived from?...
Umm... I don't see any numbers in bold type
The √3 operand should be obvious. The 1000(A) is given, as is the 50% power factor (which is the .5 in the equation, because
cos θ = PF, as noted in my previous post). The .00163 is resistance in ohms per distance unit(s).?generally that is 1000 ft. working in the imperial system of measures. ...And the 0.00093 is inductive reactance, in the same ohms per distance measure.
...Than the Xsin? is equal to the X value (at 60hz) /1000 ???
but where does the 0.866 come from?? The sin of 60 is .866 is that for the frequency??
No... 60 is theta(
θ) in degrees (i.e. 60?). X, more appropraiately X sub L is the inductive reactance portion of the impedance in ohms per 1000 ft. (?). That value has already taken 60Hz operation into consideration. What multiplying X by
sin θ does is it adjusts X for the current's phase shift from the applied voltage...