The former IEEE formula used those terms. The terms provided are also equivalent to the formula at the very end of the Notes to Table 9, where...charlie b said:I haven't seen a voltage drop formula that uses those terms.
The values for R and XL are in the preceding columns (i.e. if one reads left to right :wink: )But I think you can get what you need from Table 9. The column showing "Effective Z at 0.85 pf" can be used to calculate R and X.
Umm... I don't see any numbers in bold typeMike01 said:In a square d catalog for busway systems it gives an example for 1000A 50% pf bus duct as follows:
Sqrt(3) * I (R cos? + X sin?)
Sqrt(3) * 1000 (.00163 *.5 + 0.00093 * .866)
What I do not understand is where are the numbers in bold derived from?...
No... 60 is theta(θ) in degrees (i.e. 60?). X, more appropraiately X sub L is the inductive reactance portion of the impedance in ohms per 1000 ft. (?). That value has already taken 60Hz operation into consideration. What multiplying X by sin θ does is it adjusts X for the current's phase shift from the applied voltage......Than the Xsin? is equal to the X value (at 60hz) /1000 ???
but where does the 0.866 come from?? The sin of 60 is .866 is that for the frequency??
Cos? and Sin? come from the power factor. PF = 0.50Mike01 said:In a square d catalog for busway systems it gives an example for 1000A 50% pf bus duct as follows:
Sqrt(3) * I (R cos? + X sin?)
Sqrt(3) * 1000 (.00163 *.5 + 0.00093 * .866)
What I do not understand is where are the numbers in bold derived from?
If I am right the R cos? is equal to the R value given 1.63/1000 ???
Than the Xsin? is equal to the X value (at 60hz) /1000 ???
but where does the 0.866 come from?? The sin of 60 is .866 is that for the frequency??