Just looked at a job where a school is getting a walk-in freezer.
I've only hooked up one before, and it's been a few years so I just wanted to throw out a few questions...
This freezer isn't assembled yet so I was only able to look at the components on pallets on the ground.
The condenser unit (mounting on top of freezer) is 208v 3-phase. Min ckt amps is 16.1, max breaker is 20amps.
The inside unit cooler is 208-230v 1phase. Nameplate shows an MCA 1.1 and a MOPD OF 20.
This nameplate also shows the "(Defrost) Heater Circuit", 230volts, 1phase, 7.8 amps, 1800 watts.
I'm assuming I need to run 2 circuits, a 3-phase 20 amp circuit for the condensing unit (3-pole disconnect on top of unit by condenser), and a 1-phase 20 amp circuit for the inside unit cooler?
Also, locating the disconnect for the inside unit cooler- is it common to mount that disconnect inside the unit adjacent to the cooler? I seem to remember using a 20 amp 2-pole toggle switch for this previously?
I'm assuming the 2 units talk to each other with low-voltage wiring? Guess I'll have to check with the HVAC company and see who's responsible for that...
Anything else I should be aware of?
Thanks!
Thanks!