LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
It does if the water is cold enough!georgestolz said:Does cold water create a shock hazard?
It does if the water is cold enough!georgestolz said:Does cold water create a shock hazard?
I agree with you George. The wording in 250.104(A) tells us metal water piping systems shall be bonded. It makes no reference, as found in 250.104(B), to "that may become energized". So, to me, for them to use the language found in 250.104(B) for Other Metal Piping to turn down the proposals seems quite curious. You could very easily have a metal water piping system with a non-metallic fitting (a filter or the like) that would prevent the entire system from being bonded. And just as easily on the same system it would be possible that there is nothing of an electrical nature connected to this piping system (electric water heater, water softener, etc.) that would provide an equipment ground that would be used for this bond as they suggest. So are we to just leave this section of metal water piping unbonded?georgestolz said:Does anybody else get the impression they are adding an undue amount of inflection to make this statement hold water? I feel like they're blowing smoke up our butts.
What is the bonding of metal water pipes for at all, if they're perfectly content to not bond half of them? Does cold water create a shock hazard?
I think what this is Mike is a strict interpretation of 250.104(A)(1). If you have a cold water piping system and a hot water piping system, they both need to be bonded (if they aren't already tied together by the plumbing itself). I really don't think this is a case of the "mean 'ol inspector" trying to make the electrician do more work, but a case of "the book says metal water piping systems must be bonded, so bond it". I always jumpered around those things that interrupted the continuity of the piping when I was contracting without being told by the inspector.jwelectric said:What I am looking for is something that would substantiate an inspector requiring a bonding jumper to be installed between the hot and cold water pipes.
There are some inspectors in this country that feel that this is a requirement when installing a bonding conductor as outlined by 250.104 but I just can?t find anything that will substantiate this in the code.
By what rule could this be enforced?
mvannevel said:I think what this is Mike is a strict interpretation of 250.104(A)(1). If you have a cold water piping system and a hot water piping system, they both need to be bonded (if they aren't already tied together by the plumbing itself).
mvannevel said:I really don't think this is a case of the "mean 'ol inspector" trying to make the electrician do more work, but a case of "the book says metal water piping systems must be bonded, so bond it". I always jumpered around those things that interrupted the continuity of the piping when I was contracting without being told by the inspector.
I can?t answer this question until my original question gets answered.mvannevel said:I really agree with George here. If all of the piping doesn't have to be bonded, then why bond any of it?
jwelectric said:
Would not the hot and cold come from the same water system?
Is there truly two different systems or just one?
Neither do I think that this is a case of the inspector trying to be mean or ugly but I do believe that it is a simple case of not understanding what is being asked for by the code.
Pray tell me what makes then different metal piping systems.mvannevel said:Mike-They may come from the same water system, but that doesn't necessarily mean they are the same metal piping system.
The same people that writes this section of the code are saying to use subsection (B) in the case of an insulating fitting being inserted in the system. Why are they saying this?mvannevel said:250.104(A)(1) makes no mention of metal water piping systems that are likely to become energized. It only references metal water piping systems. 250.104(B) refers to other metal piping systems that may become energized. These two are clearly not the same thing.
jwelectric said:The same people that writes this section of the code are saying to use subsection (B) in the case of an insulating fitting being inserted in the system. Why are they saying this?
Ditto. Those panel statements make 250.53(D)(1) make even less sense than it did, which a feat.mvannevel said:That's a good question Mike. One I wish I knew the answer to.jwelectric said:The same people that writes this section of the code are saying to use subsection (B) in the case of an insulating fitting being inserted in the system. Why are they saying this?
If that's the case (and I'm not saying it isn't), why bond around them when the underground portion of the pipe is used as a grounding electrode? After all, it should, in theory, work the same way you described above to drain off this stray voltage that may be conducted by the water whether you bond around them or not. And what if it's a completely nonmetallic water piping system from the outside into the house consisting of all plastic or pvc? The only metal here would be the submersible pump (which would maybe be covered under 250.104(B)?). Would we then be worried about stray voltage or lightning only on the water itself (providing there was a high enough TDS level to make it conductive)?jwelectric said:When the metal water pipe is not being used as an electrode the bonding the metal water pipe will drain off any stray voltages strong enough to be conducted by the water such as imposed by lightning or any fault condition that may occur and the bonding around things such as filters and water heaters are not required and 250.104(B) takes over as outlined by the comments of the code panel.
I'm trying to understand this better myself. I don't want to require something that the code doesn't. I may well be all wet when it comes to my understanding of bonding and the reasons we do so. These are all things taught to me by instructors, electricians, and inspectors as I was learning the trade. That doesn't automatically make them right, I know, and it's indeed possible that I was taught wrong. I'd like to look into this closer myself. Where did the information that you posted on the stray voltage aspect of this come from?jwelectric said:I welcome any and all comments on this matter as I myself am trying to better understand how an inspector can require a conductor to be installed around a water heater when there is no requirement to do so to be found in 250.104 for bonding a metal water pipe.
mvannevel said:If that's the case (and I'm not saying it isn't), why bond around them when the underground portion of the pipe is used as a grounding electrode?
I don?t buy it either but I got in some good typing practice while typing it.georgestolz said:I don't buy the stray voltage theory.
I would think that we should hire a voltage control officer similar to the animal control officer to catch all the stray voltages and fine the owner if the stray voltages don?t have the proper voltage tags.georgestolz said:You're bringing it into the structure. Now where is it going?
By What? Where will the current come from that will produce the shock? In 250.104(B) we are instructed to bond any pipe that in likely to become energized and are allowed to do this bonding with the equipment grounding conductor that is ran with the circuit conductors.georgestolz said:With a hot-cold seperation, then the cold could shock the user completing a path on the hot. Same problem, different path, same difference.
I am seeking this answer and shall not stop until I find it.georgestolz said:I don't have an answer.
That pretty well sums up my confusion Mike. 250.104(A)(1) makes no mention whatsoever about interior metal water piping "that may become energized" It merely instructs us to bond this piping. I see your argument that it doesn't say we have to bond every inch of this piping, but following that line of reasoning, it also doesn't say we only need to bond a few feet of it either. Or bond up to the first insulating joint. As I said earlier in this thread, the way I read it, I'm being instructed to bond all of the interior metal water piping system regardless of whether or not it may become energized.jwelectric said:By What? Where will the current come from that will produce the shock? In 250.104(B) we are instructed to bond any pipe that in likely to become energized and are allowed to do this bonding with the equipment grounding conductor that is ran with the circuit conductors.
I'm guessing for the same reason it needed to be bonded in the first place. If it makes sense for us to bond this metal piping system at all (even though it's not being used as a conductor or an electrode), then it also makes sense that the whole system should be bonded.jwelectric said:The other part that I seem to be missing is the desire to keep it electrically continuous. It is not being used as a conductor nor an electrode so why does it need to be continuous?
The hot could have contact to the earth through other means (by chance).jwelectric said:By What? Where will the current come from that will produce the shock? In 250.104(B) we are instructed to bond any pipe that in likely to become energized and are allowed to do this bonding with the equipment grounding conductor that is ran with the circuit conductors.
I think the answer is, the panel has not thought this through entirely (as much as it pains me to say it).I am seeking this answer and shall not stop until I find it.
So to follow what you are saying, a system that has nonmetallic pipe but does have metallic stubs a bonding conductor sized by 250.66 would need to be installed at each stub and bonded back to the service. This would ensure that all metal pipes are bonded.mvannevel said:That pretty well sums up my confusion Mike. 250.104(A)(1) makes no mention whatsoever about interior metal water piping "that may become energized" It merely instructs us to bond this piping. I see your argument that it doesn't say we have to bond every inch of this piping, but following that line of reasoning, it also doesn't say we only need to bond a few feet of it either. Or bond up to the first insulating joint. As I said earlier in this thread, the way I read it, I'm being instructed to bond all of the interior metal water piping system regardless of whether or not it may become energized.
What I am looking for is something concrete that will take all the guess work out of the facts. One thing that is a fact is that 250.104(A) has only one requirement for this bond and that is for it to be accessible.mvannevel said:I'm guessing for the same reason it needed to be bonded in the first place. If it makes sense for us to bond this metal piping system at all (even though it's not being used as a conductor or an electrode), then it also makes sense that the whole system should be bonded.
250.4 in its entirety is talking about electrical conductive material and electrical equipment and it is not addressing the grounding electrodes, metal air ducks, metal waste pipes, metal drain pipes, metal air pipes, metal sprinkler pipes nor metal water pipes. These are addressed in 250.52 and 250.104.mvannevel said:Here's where I see things having gone terribly astray. 250.4(A)(4) Bonding of Electrically Conductive Materials and Other Equipment talks about electrically conductive materials that are likely to become energized. 250.104(B) also mentions the phrase "that may become energized". However, this wording was not included in 250.104(A)(1). Why?
The fact that it has been written in the code like this for at least the past 44 years is the reason for my question in the first place.mvannevel said:It's been that way a long time, so I find it hard to reason that it was an accidental omission. Maybe (as I also mentioned earlier) this is either a case of poor code writing, or poor substantiation. I'm willing to believe that the intention is to have all of the metal water piping system bonded. Therefore, it's not necessary to mention the likelyhood of becoming energized or to bond around items that interrupt the continuity. Those are givens. I'm also willing to listen to anybody who can show me that this was never the intent of the code.
georgestolz said:One other chafing point I have: I submitted a proposal to change 250.104, and then another for 250.104(A)(1).
georgestolz said:
Either I somehow forgot to print it (because I'm looking at it right now on my computer, all ready to go) or they lost it. The answer to the proposal might have shed more light on this.
No, not at all. That would not constitute a metal piping system, and wouldn't require bonding to those metal stubs.jwelectric said:So to follow what you are saying, a system that has nonmetallic pipe but does have metallic stubs a bonding conductor sized by 250.66 would need to be installed at each stub and bonded back to the service. This would ensure that all metal pipes are bonded.
Actually, to me, there are two requirements. One is to bond the system, and the other is that the bonding be accessible. But I've got to agree that it would be nice to find something that takes the guesswork out of this.jwelectric said:What I am looking for is something concrete that will take all the guess work out of the facts. One thing that is a fact is that 250.104(A) has only one requirement for this bond and that is for it to be accessible.
Yes, but you'll notice that 250.4(A)(4) is Bonding of Electrically Conductive Materials and Other Equipment. I'd say that the metal water piping system falls into this category. And 250.4 contains the General Requirements for Grounding and Bonding. These are then modified by the requirements found in 250.104.jwelectric said:250.4 in its entirety is talking about electrical conductive material and electrical equipment and it is not addressing the grounding electrodes, metal air ducks, metal waste pipes, metal drain pipes, metal air pipes, metal sprinkler pipes nor metal water pipes. These are addressed in 250.52 and 250.104.
jwelectric said:In 250.4 and 250.53(D) the panelist made a point to ensure that continuity was maintained in those sections. It is my opinion that the omission of this requirement in 250.104 was not an oversight on the part of the panel and was never intended to be part of the rule. I base this on the remarks from the panel as posted.
This is where it gets curiouser and curiouser to me. Do they mean to say that if a metallic water piping system has an insulating joint or a short non-metallic pipe at some point, that its not a complete system and therefore doesn't fall under 250.104(A) at all? Does it then follow that we needn't bond it at all? If we follow the wording of 250.104(B) and it's not likely to be energized I'd guess not. But then to follow their logic, does 250.104(B) only apply to complete piping systems as well? I don't see the word "complete" in either one of those sections.Panel Statement: The requirements of 250.104(A) apply to complete metallic water piping systems. Where there is no complete metallic water piping system, then the requirements of 250.104(B) would apply for those portions of isolated metal water piping system likely to become energized.
I'm looking for that concrete evidence myself. I'd guess we'd need to see their substantiation for the bonding conductor to that water pipe in the first place. Then explain why it needs to be based on the service conductors. And then explain if and why a bonding jumper would be required and how it should be sized.jwelectric said:I am looking for something a little more concrete than a guess, opinion or belief. Give me something that would substantiate the need for a jumper sized by the service conductors. Show me how this much current can ever get on the water line that in not part of the grounding electrode system.