LarryFine
- Henrico County, VA
- Electrical Contractor
So, just how long does a continuous section of metallic pipe need to be to be considered a system?
Then how much pipe must be required before we have a piping system? Could the short pieces be argued as easily as the hot water pipe?mvannevel said:No, not at all. That would not constitute a metal piping system, and wouldn't require bonding to those metal stubs.
This is the part that I am having a hard time dealing with. Where is the guess work found in this section? It is very clear to me, make it accessible and be done.mvannevel said:Actually, to me, there are two requirements. One is to bond the system, and the other is that the bonding be accessible. But I've got to agree that it would be nice to find something that takes the guesswork out of this.
Now I must ask you to address the part of that section that says ?Electrically conductive materials that are likely to become energized? and explain how it is going to become energized.mvannevel said:Yes, but you'll notice that 250.4(A)(4) is Bonding of Electrically Conductive Materials and Other Equipment. I'd say that the metal water piping system falls into this category. And 250.4 contains the General Requirements for Grounding and Bonding. These are then modified by the requirements found in 250.104.
We don't know how much pipe constitutes a system because they don't define it. I say short stubs of pipe aren't a system, but long runs of hot water piping are. Other inspectors may (and probably do) see it differently. And our problems are only beginning with this lack of a definition.jwelectric said:Then how much pipe must be required before we have a piping system? Could the short pieces be argued as easily as the hot water pipe?
While it's very clear to you, that it only need be accessible, to others (me for example) it still hasn't been made clear. Make the connection to an isolated portion of the piping accessible? The section says piping system, and I take that to literally mean the entire system.jwelectric said:This is the part that I am having a hard time dealing with. Where is the guess work found in this section? It is very clear to me, make it accessible and be done.
More confusion. Why do they talk about likely to become energized in one location, and omit it in another? To me, 250.104(A)(1) either modifies the requirement in 250.(A)(4) or they've left something out. Which do you think it is?jwelectric said:Now I must ask you to address the part of that section that says ?Electrically conductive materials that are likely to become energized? and explain how it is going to become energized.
Also if we are going to bring 250.4 into this discussion and use it to insure that the water pipe is continuous would we not also have to conform to 250.8 also?
If so would we be required to install a jumper sized by 250.66 at each sweated joint in a copper water pipe?
Well, not exactly. It used to say that, but it doesn't anymore.jwelectric said:They say the same thing that they have always said and that is to bond those parts that are likely to become energized.
mvannevel said:For what it's worth, even Soares Book on Grounding makes mention of ensuring that the hot and cold piping are bonded together (just as Mike Holt does). And I still happen to think that if it's that important that we bond this piping when it's not being used as an electrode, then it's probably just as important that we bond all of it. If it's not important enough to bond all of it, then we serve no purpose by bonding only a portion of it. The Panel needs to make up their mind one way or another.