:lol:
They use plastic water meters out there? :huh:
Don't know I haven't seen one
:lol:
They use plastic water meters out there? :huh:
Don't forget hot to cold bond at water heater.
I've seen this done a lot with older homes around here. Was that in the code at some point? We don't do it around here anymore.
Don't forget hot to cold bond at water heater.
Thanks for all the responses. It seems that with a commercial building served by a common water line (metallic) that is underground with individual waterline taps (also metallic) that run underground and up into each individual tenant space that have their own water meter, we are able to bond each individual tenant space panel board using 250.66 based on the feeder size. I still get a bit confused; i thought that with a main service disconnect that the water line main was to be used as part of the grounding electrode system using Table 250.66. I have read that most comments seem to state that Table 250.122 can be used as bonding the metallic water line even though the water line is not metallically isolated from the other tenant spaces. Article 250 is not always easy to understand.
ANY FURTHER COMMENTS ? ]