Jaybone812
Senior Member
- Location
- Massachusetts-2023 NEC
- Occupation
- Commercial & Residential Electrician
250.68(C)(1) doesn't actually clearly say that. The first sentence is a permission, not a requirement or prohibition. The second sentence only applies to interconnecting multiple electrodes. There is nowhere in the code that unambiguously requires the GEC connection to the water pipe to be within 5ft of the entrance.
If want the underground water pipe to be your grounding electrode you absolutely have to connect the gec within 5’ of entry . The interior water pipe you connect to is allowed to extend your gec connection to the underground water pipe electrode if you connect within 5’ .
So you’re incorrect it’s definitely saying if you want to use the actual underground water pipe as a grounding electrode a gec must connect within 5’ of entering the building
Sent from my iPhone using Tapatalk