My question for you is this:
What if you have a conduit entering dead center on the top of a panel from a roof penetration. Let's say the sealing compund gave way and now you have water leaking through and did NOT have rain-tight fittings.....would this save the main busbar?
What is the purpose of the rain tight EMT couplings/connectors when the conductor inside is wet location rated?It doesn't make sense.
When the CMP approved this did they question it a bit?
Why doesn't it make sense to minimize the intrusion of water into a raceway system?
Chris
If that is an issue why are we permitted to use straight threaded conduit couplings? Rigid couplings leak a lot more than the old compression type EMT couplings.Why doesn't it make sense to minimize the intrusion of water into a raceway system?
Chris
The reason that water collects in PVC is condensation from air in the raceway not from water entering from the ground. If you take and use primer and PVC glue on all the joints you will still have water in the raceway due to condensation.
Chris
My question for you is this:
What if you have a conduit entering dead center on the top of a panel from a roof penetration. Let's say the sealing compund gave way and now you have water leaking through and did NOT have rain-tight fittings.....would this save the main busbar?
If that is an issue why are we permitted to use straight threaded conduit couplings? Rigid couplings leak a lot more than the old compression type EMT couplings.
8-134 Log #591 NEC-P08
(358-42)
Final Action: Accept
Submitter: Vince Baclawski, National Electrical Manufacturers Association (NEMA)
Recommendation:
Revise text to read as follows:
Couplings and Connectors. Couplings and connectors used with EMT shall be made tight. Where buried in masonry or concrete, they
shall be the concretetight type. Where installed in wet locations, they shall comply with 314.15(A) be the rain tight type.
Substantiation:
Section 314.15(A) requires such fittings to be listed for use in wet locations. EMT is permitted for use in many types of wet locations.
Some wet location applications might require greater or lesser degrees of protection from the ingress of moisture as allowed for in the
first sentence of 314.15(A) "...so as to prevent moisture from entering or accumulating..." the term "Raintight-type" unnecessarily limits
the applications for EMT systems within the full scope of wet location applications.
Panel Meeting Action: Accept
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13
Ballot Not Returned: 1 Cox
930
The wet location standard was added by a proposal from NEMA with the intent to do nothing more than align EMT fittings used in wet location with the requirements in Article 314.
Rob, I am not following you here.
It was my understanding we were talking about the UL listing change that made all the EMT compression fittings we have used in the past as no good and now when ordering compression fittings you have to ask for the new wet location type.
That's possible and could have been the resaon for the proposal. Or it could have been the other way around, the NEC changed the requirment and then the listing agency followed the new code wording.
The wet location standard was added by a proposal from NEMA with the intent to do nothing more than align EMT fittings used in wet location with the requirements in Article 314.
That does not address my question. Why is water intrusion only an issue with. EMT? If water tight couplings are really necessary why does NEMA Cal for the use of tapered threads for rigid conduit couplings. The now used straight thread couplings leak more than the EMT couplings that were used in the past.
... Why is water intrusion only an issue with. EMT? Politics maybe. f water tight couplings are really necessary why does NEMA Cal for the use of tapered threads for rigid conduit couplings. The now used straight thread couplings leak more than the EMT couplings that were used in the past.
who is going to make more money by requiring tapered threads?
My question for you is this:
What if you have a conduit entering dead center on the top of a panel from a roof penetration. Let's say the sealing compund gave way and now you have water leaking through and did NOT have rain-tight fittings.....would this save the main busbar?
The reason that water collects in PVC is condensation from air in the raceway not from water entering from the ground. If you take and use primer and PVC glue on all the joints you will still have water in the raceway due to condensation.
Chris