1)I though the whole purpose if this thread was to reduce the costs of the penetration. I would expect the labor and material to provide boxes on each side would far exceed the cost of an actual bulkhead fitting.Ok so say you have Rob's running thread idea. I see several options from there:
1. But a box on the inside and the outside with locknuts. What could be wrong with that?
2. What about a RGS coupling and a 90 degree flex/sealtight connector on that? IS that one of those silly academic things where we cant thread a connector into a coupling? I just did that today LOL.
2) A coupling on the running thread? That is specifically prohibited in 344.42(B).