No, it's basically saying that in addition to your electrode lead and your work lead clamp, you ALSO make sure your weldment is grounded. It's a completely separate issue. In this type of situation, though, it's automatic because the grounding is also the work connection. It won't always be.
Unless I'm missing something, infinity's picture just shows the work connections. The work connections should NOT be just connected to something that's grounded on the assumption that the work piece is also grounded. Any poor connection along the return path will be another welding location. Seems like a good chance that's what happened in this situation. I hope you are not advocating doing that way.