I blame "nerf balls" for this. I know it sounds crazy, and ok, maybe it wasn't the nerf balls. But I really think young guys need to smash a finger, skin a knuckle, get burned a little, and know what a electrical shock feels like. No pain = no gain
I really don't know what you are trying to say here. Are you saying that it is not enough to stand over a hole to know that it is dangerous? You think that you actually need to fall into the hole to know that there is a hazard there??
http://www.millerwelds.com/resources/articles/welding-Safety-prevention-scheduled-maintenance/
1. The Power Source and Primary Power Line
Grounding the Equipment
Welders must be concerned at all times about the possibility of electrical shock. Wet working conditions must be avoided, because water is an excellent conductor and electricity will always follow the path of least resistance. Even a person's perspiration can lower the body's resistance to electrical shock. Standing on a dry rubber mat or, when welding outdoors, standing on a dry board is always advisable. Poor connections and bare spots on cables further increase the possibility of electrical shock, and therefore, daily inspection of these items is also recommended.
Aside from these more obvious shock hazards, equipment operators should routinely inspect for proper ground connections. A proper ground connection is always necessary because it provides a safety connection from a welding machine frame to the earth. Connections typically used for grounding an engine-driven welding machine include a cable connected from a ground stud on the welding machine to a metal stake placed in the ground.
The workpiece being welded and the frame or chassis of all electrically powered machines must be connected to a good electrical ground. This can be accomplished by connecting it to a properly grounded building frame or other appropriate ground. Chains, wire ropes, cranes, hoists and elevators must never be used as grounding connectors.
The work lead is not the grounding lead. The work lead connects the work terminal on the power source to the workpiece. A separate lead is required to ground the workpiece or power source.
When arc welding equipment is properly grounded according to the National Electrical Code, and to ANSI Z49.1 "Safety in Welding and Cutting" standards, a voltage may safely exist between the electrode and any conducting object. Examples of conducting objects include buildings, power tools, work benches, welding power source cases and workpieces. Never touch the electrode and any metal object unless the welding power source is off.
When installing a welding system, connect the frames of each unit such as welding power source, control, work table and water circulator to the building ground. Conductors must be adequate to carry ground currents safely. Equipment made electrically hot by stray current may deliver a powerful shock. Never ground to an electrical conduit, or to a pipe carrying any gas or flammable liquid such as oil or fuel.