The specific problem occurred at a loaction where the service to several houses along a street where served by transformers located on poles along the back line of the properties. Each house has a pool. In many cases, the pools are only 5 linear feet from the utility poles themselves. This created a very low impedance path for normal current to flow as the pool bonding grid was effectively earthed and connected to the equipment grounding conductor for the pool equipment. More than 50% of the normal operating current would be present at metal parts of the pool structure.
I consider a good percentage as more than is necessary, meaning, it can be effectievely reduced.
Using a well casing as a GEC will not provide as low enough impedance path to allow the operation of the OCD, even if coonected with a #4 and directly to the main bonding location. You don't want fault current to use the GEC system, you want it to use the service grounded conductor. My example above would and could carry fault current as well as normal operational current, and that in my opinion is bad design.
The specific problem occurred at a loaction where the service to several houses along a street where served by transformers located on poles along the back line of the properties. Each house has a pool. In many cases, the pools are only 5 linear feet from the utility poles themselves. This created a very low impedance path for normal current to flow as the pool bonding grid was effectively earthed and connected to the equipment grounding conductor for the pool equipment. More than 50% of the normal operating current would be present at metal parts of the pool structure.
I consider a good percentage as more than is necessary, meaning, it can be effectievely reduced.
Using a well casing as a GEC will not provide as low enough impedance path to allow the operation of the OCD, even if coonected with a #4 and directly to the main bonding location. You don't want fault current to use the GEC system, you want it to use the service grounded conductor. My example above would and could carry fault current as well as normal operational current, and that in my opinion is bad design.