A two part question here, both involving a sewer pump I did a while back:
First, what does the code say about the listing requirements of cables and conductors in open bottom outdoor junction boxes? We have a state level code that requires that they must be listed for direct burial unless certain requirements are met and in that case they only need to be listed for wet locations. Cant find anything in the NEC that mentions these boxes.
Secondly, If a pvc junction box that is listed for wet locations is installed in a wet location, is the inside of the box ever considered a wet location? I had this setup and the inspector required wet location wire nuts which I thought was strange.
Regards
First, what does the code say about the listing requirements of cables and conductors in open bottom outdoor junction boxes? We have a state level code that requires that they must be listed for direct burial unless certain requirements are met and in that case they only need to be listed for wet locations. Cant find anything in the NEC that mentions these boxes.