Was that to find one of the errors or both?
i just got a correction to put a LABEL on a stinkin gen set input recept. are you kidding me? bonded or floating neutral system? does it MATTER? The recept has FOUR wires in it no matter what so who the hell cares? i think this is another PANT LOAD!
2014 NEC 702 .7 -(C)
Where a power inlet is used for a temporary connection to a portable generator, a warning sign shall be placed near the inlet to indicate the type of derived system that the system is capable of based on the wiring of the transfer equipment. The sign shall display one of the following warnings: WARNING FOR CONNECTION OF A SEPARATELY DERIVED (BONDED NEUTRAL) SYSTEM ONLY or WARNING FOR CONNECTION OF A NONSEPARATELY DERIVED (FLOATING NEUTRAL) SYSTEM ONLY
All i see this is another way for the state to get more money out of me, for Trip Fees. No matter what the system is an Interlock is going to keep from backfeeding either one of them. iF they are worried about somebody not knowing if they are feeding a sub or a main panel, then why don't they require the label to say THAT instead of this BS about bonded or floating Ns?
RANTING!!!:rant::rant::rant:
Two requirements are at play here.
1) The first of which you mentioned above is the new requirement in the 2014 NEC NEC 702 .7(C) that requires you to label the portable generator connection inlet based upon the way in which you installed and wired the transfer equipment. This requirement has existed in the UL "White Book" for a number of years, the NEC was finally updated to the same. The required label MUST also be fully compatable with 2014 NEC 110.21(B).
2) The second requirement effective 01/01/2015 comes from the CPSC (Consumer Products Safety Commission) that requires ALL portable generators 15Kw and smaller sold in the U.S. to have ALL power outlets GFCI protected. This requires the neutral to be bonded to the frame.
While you can technically remove the neutral-frame bond and create an un-bonded "Non-Separately Derived" generator, given that you are removing a "required" safety device from a consumer product this is in MHO a very unwise decision. Before proceeding in this manner you should seek legal advice from a competent attorney.
Given the two requirements noted above, as of 01/01/2015 our policy regarding portable generator inlets and transfer switches is that we will ONLY install them in the "Bonded Neutral/Separately Derived System" configuration in a manner that is fully compliant with the two requirements noted above. This will also require that you drive a separate ground rod at the generator connection location.
Try this site :Does anyone have a source for those labels?
Since it will be outdoors, we are really looking for engraved plastic at a minimum.
I'm with you. I don't look for the gen-set business. If it happens to come my way I take it. Otherwise, it seems to be a cut-throat business in my area. I used to get a fair amount of $$$. Now other EC's are beating my prices by thousands of $$$. They're going in with low #'s hoping to get the maintenance business after-market. They can have it IMHO.thanks for that link Goldstar. i think i'm done with generators. i get one call a year at best. who needs them?
As a practical matter how do you achieve this? Are you saying that you are installing switched neutral transfer switches in all cases?
thanks for that link Goldstar. i think i'm done with generators. i get one call a year at best. who needs them?
If the neutral isn't bonded somewhere, fault current to ground can't find a path to trip overcurrent protection. That's the problem.