NickJoh
- Columbia, SC
- Retired Engineer
Thanks . I re-read your explanation and now think I understand.Both. And more to the point, the difference between the two.
Sorry I did not make it clear" My start capacitor measures 138 mfd so it is good but the other capacitor -the run capacitor - is open. I confused things by reporting the motor says "jet pump duty" but it is not a jet pump. It is a Burks 20AW6 pump. The run capacitor is so old and totally black with hardened rust or scale I can't read any markings and so far have not been able to get its value from Century, I tried cleaning it with alcohol and finally sanded the bottom looking for stamped imprits to no avail, ThanksIf a motor only has one cap, is a starting cap. If it has two caps, one is starting, the other is running. Jet pumps wouldn’t need a Cap-Start / Cap-Run (CSCR) type motor, they use a CSIR (Cap-Start / Induction-Run) motor type, so that’s a Start cap.
If a Start cap is failed, the motor will not start and will trip the breaker. The question is, why is the Start cap bad? The usual cause is that the centrifugal switch in the motor has welded, so the cap was left in the circuit all the time, and start caps are not rated to do so. This means that if all you do is replace the cap, it will fail in short order. You likely need to fix the centrifugal switch first.
Other than verifying the start cap is fine (138 MFD) and the run cap is open I have done nothing. There was nothing strange - no bearing noise - coming from the pump which started up fine and ran the sprinklers for at least awhile this year but since it runs at night I really can't say it didn't develop. My plan was to replace the open run cap and see if it would start (not trip the breaker) and if that worked then I hoped to come back with the proper value run capacitor. If it doesn't work I will replace the pump and motor.30 years old.
Have you used a Megger on it yet?
Bearings good?
Thank you again! Your post was by far the most helpful. Definitely 5 Star on a scale of 1 to 5. I couldn't allow it to remain buried among all the others some of which would not even rate a 1,I have a 2 HP pool pump that uses a 145 uF start cap and 35 uF for the run. I texted a friend who installs pools and asked him to look at other pumps he has and he had a 2 HP that used 120 uF start and 45 uF run, so I'd bet that anything between 100 and 150 for start and 30 to 50 uF for run would be just fine
My experience has been CSIR is usually 1.0 HP and less, occasionally 1.5 HP. 2.0 HP and up almost always is CSCR.If a motor only has one cap, is a starting cap. If it has two caps, one is starting, the other is running. Jet pumps wouldn’t need a Cap-Start / Cap-Run (CSCR) type motor, they use a CSIR (Cap-Start / Induction-Run) motor type, so that’s a Start cap.