The new 100-A breaker was running for extended periods with 115 amps running through it.
Prolonged operation above the 80% enclosed rating will likely cause eventual connection failure due to overheating.
WE see thermally damaged circuit breakers all the time that are not tripped or tripping.
I do not know what prevents the design engineer to select or the maintenance engineer to replace a breaker with a suitable time-current characteristic in consultation with its manufacturer so that the damage to its terminals or associated wiring of the breaker is avoided by the timely tripping of the breaker on any over load above its setting.