In the olden days, we bonded the modules to a wire EGC, bonded the wire EGC to the various parts of the rack, then took that wire EGC and bonded it to the inverter ground connection. That was bonding and we liked it.
Then the WEEB came along and the need to bond the module to the racking was done by the WEEB and the bonding of the racking together and to the inverter ground was done by a wire EGC. But racking was a collection of parts that were bolted together and those connections were not evaluated as electrical bonds. So all the parts of the racking still needed a connection to a wired EGC. The introduction of UL 2703 allowed the racking and all its connections to be listed as an EGC, so then you just had to connect one point on the racking to the inverter with a wire EGC. After the introduction of UL 2703 the use of WEEBs to connect modules to unlisted racking was no longer allowed.
You can still use unlisted racking, but you are back to the old school method of connecting all the parts together with a wire EGC.
Just because an AHJ does not reject the work does not certify that the work is code compliant, nor does one AHJ's acceptance then require another AHJs to accept it.