kbsparky

Senior Member
Location
Delmarva, USA
It's funny. Today I tried to land second conductor on afci breaker SqD 20A hom with pressure plate but it had entry for only 1 conductor. Neutral terminal had completaly exposed pressure plate.

Square D Arc-fault and GFI breakers are not rated for more than 1 conductor on their terminals.

Only their standard breakers 30 Amps or less have the dual terminal capacity.
 

arknack

Member
Location
Jackson, MI
Neutral

Neutral

Yes, I agree, I did not read carefully enough. I had assumed his 'two wire 120 volt circuit' was a typical household branch circuit not a 120 volt transformer.

In my corner of this industry I almost never deal with a 120 volt circuit that comes from a straight 120 supply.


I would bet heavily that arknack was thinking of a typical branch circuit as well.

Yes I was. Looks like I still have a lot to learn. I'm still having problems wrapping my head around this.
 