It's funny. Today I tried to land second conductor on afci breaker SqD 20A hom with pressure plate but it had entry for only 1 conductor. Neutral terminal had completaly exposed pressure plate.
Square D Arc-fault and GFI breakers are not rated for more than 1 conductor on their terminals.
Only their standard breakers 30 Amps or less have the dual terminal capacity.