I don't know if this should be in Grounding vs Bonding or here, but here goes...
I've always been taught, when using conduit of any kind, there should always be and EGC sized according to T.250.122. Where I am confused, is in 250.118, it lists EMT, RNC among others as acceptable EGC's. Does this mean that I could omit an EGC in said raceways as they themselves are an EGC? I don't understand how one would determine the effective ground fault current path for a length of, say 100' of 3/4" EMT. In order to qualify, would the length have to consist of only the conduit and fittings with no boxes in between? If this example were to have 20A #12 circuits in it, would the EMT be comparable to the #12 EGC that would otherwise be required?
I've always been taught, when using conduit of any kind, there should always be and EGC sized according to T.250.122. Where I am confused, is in 250.118, it lists EMT, RNC among others as acceptable EGC's. Does this mean that I could omit an EGC in said raceways as they themselves are an EGC? I don't understand how one would determine the effective ground fault current path for a length of, say 100' of 3/4" EMT. In order to qualify, would the length have to consist of only the conduit and fittings with no boxes in between? If this example were to have 20A #12 circuits in it, would the EMT be comparable to the #12 EGC that would otherwise be required?