A PV array is a current-limited source. An interactive inverter does not have a rotating mass and is controlled by power electronics that limit fault current characteristics. Extensive testing by NREL indicates:
"inverters designed to meet IEEE 1547 and UL 1741 produce fault currents anywhere between 2 to 5 times the rated current for 1 to 4.25ms."
That's probably not enough energy to open an OCPD. The utility grid is really the only source of fault current that matters in an interactive PV system. While I'm not an engineer, I have a hard time believing that the magnitude of these fault currents changes based on the topology of an inverter on the secondary side of the utility transformer.
Furthermore, all the test data I've seen shows that non-isolated inverters are inherently safer, by orders of magnitude, than transformer-isolated inverters in terms of detecting faults on the dc side of a PV system.
"inverters designed to meet IEEE 1547 and UL 1741 produce fault currents anywhere between 2 to 5 times the rated current for 1 to 4.25ms."
That's probably not enough energy to open an OCPD. The utility grid is really the only source of fault current that matters in an interactive PV system. While I'm not an engineer, I have a hard time believing that the magnitude of these fault currents changes based on the topology of an inverter on the secondary side of the utility transformer.