shboal11
Member
- Location
- Grand Terrace, California
i have a 200 amp sub panel 100 ft away from the main, and 15 feet below in pvc conduit. The sub is fed by 3/0 4 wire thwn and a #4 ground to a ufer at the sub. There is what appears to be calcium deposit on the outside of the feeder wires. the buss bar is burnt. The ground to the ufer is burnt in the sub panel and the wires on most of the breakers, grounds and neutrals show signs of corrosion. The cooper feeder wires are burnt and corroded ( black suit) at the sub only. the sub is also feed by 2 inverter's for solar. i have to replace both 9 year old inverters in the past 3 months. The load on this panel is primarly the 50 amps that goes to the well pump. This sum is fed about 25 amps of solar at 240. I have pictures too