why RCD ill not trip
for TNC-S when N opened the current will path from Line to PE to the electrode backing to the source through mass of Earth there will be difference between the current in Line and N so RCD have to trip ?
If N opens at the service, the power will flow through the RCD, into the load, back into the RCD, into the main panel and then get on the PE. Because of current flowing in and out of the RCD being equal, there is no trip. RCD only works on a current imbalance.