Scott -scott thompson said:...The high Voltage to Ground (from Capacitive Coupling) on an Ungrounded AC Power System, stresses the Insulation of Conductors to the point that leakages may be produced - in the form of Arcing.
...
Are we discussing re-striking, arcing ground faults? If so, I think we just made a jump to industrial grade systems. I don't know too much about this particular phenomena other than reading IEEE Red Book and IEEE std 142. I've worked on two different ungrounded 480V systems: Navy ships, and feeds to VFDs. Neither had that problem. However, for 480 systems, other than the special cases I mentioned, my preference is resistance grounded Wye.
What system voltage are we discussing? 120/240, 240D, 480D/Y, 575, ... 13.8kV. Are we still discussing arcing, re-striking, GF? Without some limitations, the statement is not something I can evaluate.scott thompson said:...Voltages to Ground on Ungrounded Systems may range from as low as 10 Volts, to as high as 1000 Volts. ...
carl