WastefulMiser
Senior Member
- Location
- ANSI World
MC connectors already have the bushing in it.
By the by, hello.
By the by, hello.
WastefulMiser said:MC connectors already have the bushing in it.
By the by, hello.
iwire said:Redheads are not required to be used on MC by the NEC.
I use them anyway as I don't find the MC connectors we use to protect the conductor as much as I like.
Jim W in Tampa said:Can you afford a short ? I see it as double protection and always use.
WastefulMiser said:I don't know about you, but I trust my work enough to sleep peacefully at night.
JJWalecka said:and tape over the sheath to hold it.
iwire said:Go easy on taping the sheath, the connector has to grab onto bare armor to provide the bonding of the armor.
infinity said:Although the MC cable is not an EGC it still is required to be grounded.
iwire said:Go easy on taping the sheath, the connector has to grab onto bare armor to provide the bonding of the armor.
celtic said:I thought the jacket on MC was not a suitable EGC unless listed as such?