Toros
- Tujunga, CA
Hi
Would tell me what is wrong with my design of the service for an apartment complex
See attached
Tanx
Two confirmations please:
Is the service really 120/240 4-wire three phase (high leg delta) with only the house panel having access to the high leg?
And is the 350 MCM calculated using the reduced size service wire allowances? You could not, IMHO, apply that when feeding multiple units and house.
If the wiring is full ampacity, I do not see a problem.
My first thought was along the line of Golddigger's question.
3 phase 240/120 ?? with a high leg ??
Secondly, the 3/0 neutral you show between neutral bars.. is it in a conduit by itself ?
Third: What is the "OH Pull" ? is this a disconnect/overcurrent device or simply a pull box ?
Last: I'm concerned about your 90amp feeders. 225.39(C) would require
a 100 amp rating.
I did not say he did. I did not have my book and so I asked.Maybe I am missing something, but how is he reducing the service conductors? he has (2) 350MCM each rated at 310Amps.
On a second note, but nothing wrong, the GEC to the CCE does not have to be 3/0.
Agree.1. Why a ground rod? Not needed AFAIK.
I believe it's 32kA SCCR.2. 32,000A service? Typo I imagine.
Bring all 3 phases to the apartment meter bank and then pick off the phases alternating, so the service will be somewhat balanced across phases.
It's a 240/120V delta.
Perhaps service transformers are open delta with large lighter, small stinger. 3? balancing would actually create a problem.Why? Is the HVAC three phase? What else would use the high leg? Why not transform it down to 208 so that the load can be balanced?
Caveat: I am an engineer, not an electrician. Be gentle with me.
How can you tell there's too much load???That 4-wire delta wouldn't fly here in Peco territory. Too much load on the A-C phase. ...
Yeah, but they usually keep track of several such open deltas on their primary and rotate the phases to balance their primary.I think he was perhaps referring to the unbalanced load, with no way to balance it.
POCO can put in a large lighting pot, but there will still be unbalance on the primary side.