Thanks, I did not see Dennis' post.See post #31
Thanks, I did not see Dennis' post.See post #31
There should be a service and installlation manual that may give you more direction.
Here is a link to UL 471 table of contents
http://ulstandardsinfonet.ul.com/tocs/tocs.asp?fn=0471.toc
It has the following entries
ELECTRICAL SYSTEM
9 Field Supply Connections
9.1 General
9.2 Permanently connected refrigerators
9.3 Cord-connected refrigerators
9.4 Grounding
They seem to make a distinction about permanently connected.
Only $716.
First off, I don't see how the customer can be upset with you over something they did, especially if they want it done to code. They should have asked you first, having gotten the information from the vendor before ordering them.
That being said, I would ask them how much/often they plan on rolling them to different areas. If you can get a constant path where they will be along/to, I would either install dedicated circuits and put a single 5-20R. If the plug cap was added after it was mfg. I see nothing wrong with changing them to 5-20P, but that might create other problems with them plugging them in just anywhere. I suppose the better way would be to just install L5-30R and just use the cap that is on the cord.
In any event, it couldn't hurt to sit down with the customer and explain your predicament.
The phrase "permanently connected" is not an instruction.
Bob:
I was poking around at Arneg websites and found only three "laval" models, and am assuming the 5'-11" model would be the Laval 6 on your label. The data sheet was a little different in that it listed MCA at 22.6A and MOP of 30A. It did have a heading of "permanent connected" on the data sheet.
Top left corner says "Made IN THE USA."
I think they lie.
The guy who screwed the door on was American - why quibble over details?
Have you decided on a plan of attack ?
Apparently you live in a different world than I.:lol:
In my world the messenger gets shot.:rant:
and carry a jelley donut with you!:lol:
I do live in a different world.:happyyes:
I said sit down and explain, not demand.
Without reading all of the other post's I would have proceeded with a 30 amp cord,plug, and receptacle with a 25 amp overcurrent protection.
I'm not so sure this piece of equipment would "Run all Day" at 18.6 amps with no problems.
If it was to run all day at 18.6 i would think it would produce a lot of heat in a 20amp breaker and eventually neusance trip.
I would however venture to say that this piece of equipment would "Run all day" with no problems on a 25 amp breaker but that's just my opinion.
I'm not so sure this piece of equipment would "Run all Day" at 18.6 amps with no problems.
I would have bought it if it was $715.