This is worse, IMO. For one thing, it says that conduit SHALL BE installed a minimum of 23mm off the roof, but then it says here's what to do if it isn't. Huh? I don't know of any other part of the code that gives a workaround for a violation.Just for clarity, yes the table is going away but the amended remnants of the rule is still in play.
View attachment 15363
For another, if the conduit is 22mm off the roof, the conductors are at ambient temperature plus 60 degrees, but if it is 24mm off the roof the conductors are at ambient? Seriously?