- Location
- Windsor, CO NEC: 2023
- Occupation
- Hospital Master Electrician
A kitchen has a sink in the corner. This corner is also the corner of the house. This sink is surrounded by a window on either side, about 8" or so from the corner. There is a receptacle installed roughly 30" from each corner, to cover the beginning of the countertops next to the sink, as required by figure 210.52.
There is 17" of "usable" counter space in this corner; measuring back 18" and sliding side to side perpendicular to the back of the sink. Being a load bearing corner, with a window immediately next to it, the corner is full of lumber.
By figure 210.52, we are required to install a receptacle there.
By 210.52(C)(5), the area immediately outside this 17" of wall counter space is behind a sink, and therefore cannot be considered suitable for a receptacle to serve the 17" space.
By physics, I can't cut out three out of five 2x4's and allow my box to bear the weight of the corner.
There is 17" of "usable" counter space in this corner; measuring back 18" and sliding side to side perpendicular to the back of the sink. Being a load bearing corner, with a window immediately next to it, the corner is full of lumber.
By figure 210.52, we are required to install a receptacle there.
By 210.52(C)(5), the area immediately outside this 17" of wall counter space is behind a sink, and therefore cannot be considered suitable for a receptacle to serve the 17" space.
By physics, I can't cut out three out of five 2x4's and allow my box to bear the weight of the corner.