My conclusions:
Ready for some controversy? If my most recent interpretation of Figure 210.52 is correct, then I feel that 89% of the members who voted (I am among them) are dead wrong.
Only the three members had it right: "Placing the receptacle in the adjacent area behind the sink" was the only correct answer to this poll.
Now, I acknowledge that it was a misnamed option, due to my misinterpretation of the code when I started the poll. If I am now correct, then there is no adjacent area behind the sink. It is not "behind the sink" as described in 210.52(C)(4). It is all counterspace as though the sink wasn't there at all.
I sincerely desire input from the members here to see if my conclusions are correct. While it would make the whole poll to appear to be a total waste of time, it would be an excellent exercise if some us suddenly learned how to read this section correctly. That's my only reason in beating this into the ground. I appreciate all the responses, and I would greatly appreciate further attention to this subject, even if you just chime in with a two word response. Thanks!
If someone needs me to repost Figure 210.52 with the color on it from a few posts back, I can. For some reason, I can't see it at the moment, I'm not sure if others can, or need it.
Edit to add: this post has a glitch in it. If you see half the text at large font, that's not my doing, please don't be irritated at me! Looks as though the new forum has some bugs in it, still...
Edit #462: I beat it into submission with some clever tricks. Looks normal now.
What should the installer be required to do (or be allowed to do)?
Omit the receptacle -- ?74%? [ 23 ]
Place the receptacle in the adjacent area "behind the sink" -- ?9%? [ 3 ]
Surface-mount a receptacle on the face of the tile -- ?9%? [ 3 ]
Cut the receptacle in anyway, code is code -- ?6%? [ 2 ]
Total Votes : 31
My conclusions:
- My incomplete description of the scenario tainted the results.
- Many votes and posts occured before I returned to find the hole in my information and fill it.
- My personal vote would have been different today than it was when I originally voted. I wonder if others feel the same way.
- Illustrations in the NEC can be widely interpreted. Since Figure 210.52 has no text supporting it, it is difficult to come to a uniform interpretation of how to implement it.
- I need to start printing bumper stickers that say "When in doubt, leave it out" and retire from the sales.
Ready for some controversy? If my most recent interpretation of Figure 210.52 is correct, then I feel that 89% of the members who voted (I am among them) are dead wrong.
Only the three members had it right: "Placing the receptacle in the adjacent area behind the sink" was the only correct answer to this poll.
Now, I acknowledge that it was a misnamed option, due to my misinterpretation of the code when I started the poll. If I am now correct, then there is no adjacent area behind the sink. It is not "behind the sink" as described in 210.52(C)(4). It is all counterspace as though the sink wasn't there at all.
I sincerely desire input from the members here to see if my conclusions are correct. While it would make the whole poll to appear to be a total waste of time, it would be an excellent exercise if some us suddenly learned how to read this section correctly. That's my only reason in beating this into the ground. I appreciate all the responses, and I would greatly appreciate further attention to this subject, even if you just chime in with a two word response. Thanks!
If someone needs me to repost Figure 210.52 with the color on it from a few posts back, I can. For some reason, I can't see it at the moment, I'm not sure if others can, or need it.
Edit to add: this post has a glitch in it. If you see half the text at large font, that's not my doing, please don't be irritated at me! Looks as though the new forum has some bugs in it, still...
Edit #462: I beat it into submission with some clever tricks. Looks normal now.