LarryFine
- Henrico County, VA
- Electrical Contractor
Now you tell us!. . . we more often have plastic enclosures on both ends.
It is very common in residential and small commercial PV installations to have plastic junction boxes on the roof, usually under the array with metal conduit jumping between mounting planes and taking the home-run down to the equipment wall. This is EMT across the roof or metallic flex if run through the attic. Most of the systems I review are either SolarEdge, which has plastic inverter wiring compartments, or Enphase which has plastic combiner boxes. So the majority of the conduit until we get to the AC disco is going from one unbonded enclosure to another.You should have included that in your opening post. Why would anyone use metallic raceways between plastic boxes or enclosures? There may be bigger problems here than bonding.
The NEC only requires that one end be bonded, wire EGC or not. Anything more is design choice.So the majority of the conduit until we get to the AC disco is going from one unbonded enclosure to another.
I work for a solar financing company and I'm currently wearing two related hats, working on design standards and reviewing PV systems post install. ...
PVC is really unacceptable in rooftop installations in this area. It's been known to degrade in the sun, it droops and touches the roof, and it looks like absolute s---. (You can't paint it to make it look nicer either, the paint peels off.) EMT is industry standard. Plastic boxes on the roof are also pretty common because you don't get metal 4X boxes that are big enough and using 3R on the roof can lead to water coming down the raceway.You should have included that in your opening post. Why would anyone use metallic raceways between plastic boxes or enclosures? There may be bigger problems here than bonding.
I once had someone complain we didn't have a grounding bushing in our bell box on the array. <facepalm>
We and many others use "Bell" boxes on the roof. They have threaded openings for conduit. Just like an LB. No bonding bushing needed. Not even possible.
In nonresidential, would a metal bell box be listed for bonding over 250V (250.97)?
They changed it to listed threaded hubs (which sucks). It is the same issue I get into with Myers hubs because not all of them are listed for it.Yes, it would fit under 250.92(B)(2). Threaded hubs.
FWIW, I checked UL 514A "Metallic Outlet Boxes" for any resistance or other electrical tests required for threaded entries, and to my surprise there are none in that standard. So maybe it does make sense that for compliance with 250.92(B)(2) the box would need to be further listed under UL 467.They changed it to listed threaded hubs (which sucks).
Why does pv grounding matter anymore than grounding anything else?We are big proponents of proper grounding so on our C&I projects we have grounding bushings on all conducts and an EGC that hits the bushing in passing. It's not an NEC requirement, but then again the NEC is kind of lenient on using a lot of things as an EGC that in my experience don't hold up over 20 years. PV grounding is just too important to our projects to leave to an EMT conduit run.
(Other than that PV wiring is pretty much guaranteed to be exposed to the elements, and therefore best practice might be to exceed code requirements ...)Why does pv grounding matter anymore than grounding anything else?
FFS if the bell box says it's UL listed that's good enough for me.FWIW, I checked UL 514A "Metallic Outlet Boxes" for any resistance or other electrical tests required for threaded entries, and to my surprise there are none in that standard. So maybe it does make sense that for compliance with 250.92(B)(2) the box would need to be further listed under UL 467.
I guess that's similar to the situation with eccentric/concentric knockouts, UL 514A requires a basic test to survive a fault and still have continuity, but it doesn't impose any maximum resistance. So if you want to use 250.97 Exception with eccentric/concentric knockouts, a separate listing "to provide a reliable bonding connection," presumably under UL 467, is required.
Cheers, Wayne
Any box used in a wet location needs to be listed per 314.15, so that's a given. The question is what the 2020 NEC 250.92(B)(2) language "Connections using threaded couplings or listed threaded hubs on enclosures if made up wrench tight" means. Do you have to use a listed hub? It's silent on integral threaded entries.FFS if the bell box says it's UL listed that's good enough for me.
I wonder what that listing would mean. Would it mean that the box is water tight or just that it won't deteriorate if it gets wet?My question to the OP is, if the plastic box is listed for wet locations what type of KO'S or hubs does it have?