LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Now you tell us!. . . we more often have plastic enclosures on both ends.
Now you tell us!. . . we more often have plastic enclosures on both ends.
It is very common in residential and small commercial PV installations to have plastic junction boxes on the roof, usually under the array with metal conduit jumping between mounting planes and taking the home-run down to the equipment wall. This is EMT across the roof or metallic flex if run through the attic. Most of the systems I review are either SolarEdge, which has plastic inverter wiring compartments, or Enphase which has plastic combiner boxes. So the majority of the conduit until we get to the AC disco is going from one unbonded enclosure to another.You should have included that in your opening post. Why would anyone use metallic raceways between plastic boxes or enclosures? There may be bigger problems here than bonding.
The NEC only requires that one end be bonded, wire EGC or not. Anything more is design choice.So the majority of the conduit until we get to the AC disco is going from one unbonded enclosure to another.
I work for a solar financing company and I'm currently wearing two related hats, working on design standards and reviewing PV systems post install. ...
PVC is really unacceptable in rooftop installations in this area. It's been known to degrade in the sun, it droops and touches the roof, and it looks like absolute s---. (You can't paint it to make it look nicer either, the paint peels off.) EMT is industry standard. Plastic boxes on the roof are also pretty common because you don't get metal 4X boxes that are big enough and using 3R on the roof can lead to water coming down the raceway.You should have included that in your opening post. Why would anyone use metallic raceways between plastic boxes or enclosures? There may be bigger problems here than bonding.