Well maybe the OP can show us what he is using.I wonder what that listing would mean. Would it mean that the box is water tight or just that it won't deteriorate if it gets wet?
Well maybe the OP can show us what he is using.I wonder what that listing would mean. Would it mean that the box is water tight or just that it won't deteriorate if it gets wet?
Frankly, I did not know about that requirement.In nonresidential, would a metal bell box be listed for bonding over 250V (250.97)?
Or is this just for the DC circuit wiring on the roof / only works in residential because they don't make them large enough for commercial?
You are right of course, but it's ridiculous, and I'm willing to go on record here to say that I literally don't care.Any box used in a wet location needs to be listed per 314.15, so that's a given. The question is what the 2020 NEC 250.92(B)(2) language "Connections using threaded couplings or listed threaded hubs on enclosures if made up wrench tight" means. Do you have to use a listed hub? It's silent on integral threaded entries.
The 2023 NEC 250.92(B)(2) language is clearer: "Connections made up wrenchtight using threaded couplings, threaded entries, or listed threaded hubs on enclosures." So any integral threaded entry suffices, and the part about "listed threaded hubs" only applies to add on hubs.
Cheers, Wayne
They don't have any pre-stamped knockouts, each one is drilled on site. Here are a couple of examples, one of which I think is pretty cool:My question to the OP is, if the plastic box is listed for wet locations what type of KO'S or hubs does it have?
When bell boxes are used as roof j-boxes we do require the enclosure itself to be bonded with a lug or terminal, that bonding transfers to the metal conduit since there is sufficient thread engagement.FFS if the bell box says it's UL listed that's good enough for me.
Right. I don't need some further proof that the threaded hubs are listed for grounding.When bell boxes are used as roof j-boxes we do require the enclosure itself to be bonded with a lug or terminal, that bonding transfers to the metal conduit since there is sufficient thread engagement.
Because PV is a source.Why does pv grounding matter anymore than grounding anything else?
Why does that make a difference? Unless a PV system is supply side interconnected, doesn't the grounding look the same as for any other feeder?Because PV is a source.
why would it matter for any source?Because PV is a source.
They are installed to be weatherproof, the snow pic was someone forgetting to close the box during install. Once buttoned up and covered with a module the boxes are weather tight, if installed correctly.So what is the point of using a plastic box if they are not installed to be weatherproof?
I'm not talking about the snow picture. The fittings used for the single conductors are not weatherproof unless they are filled with some type of compound.They are installed to be weatherproof, the snow pic was someone forgetting to close the box during install. Once buttoned up and covered with a module the boxes are weather tight, if installed correctly.
As a little side rant, yeah I hate BB and doubt they even accomplish much. They are so horribly designed. They need more lug and setscrew options around the perimeter. Also most fittings are not deep enough for the setscrew to grab, especially when you use a plastic enclosure . Finally there is no anti turn function on the lug so pretty hard to get them to stay tight in practice.Bonding bushings are the tiniest - YET most laborious - product to install PROPERLY. I avoid them like the plague.
Fair point, although the strain relief fittings do have a foam/rubber gasket that snugs around the conductors when tightened and the boxes are typically under a module, best practice is to put the fittings on the downward side of the box but even when they side enter it's good enough, they aren't meant to be submerged, if they are then there are bigger problems..I'm not talking about the snow picture. The fittings used for the single conductors are not weatherproof unless they are filled with some type of compound.
In general, nonmetallic boxes can only be used with nonmetallic cables and raceways.The NEC only requires that one end be bonded, wire EGC or not. Anything more is design choice.
Even if the far box has nothing requiring grounding? What would you connect the bonding wire to?If nonmetallic boxes are used with metallic raceway bonding at each end would be required per 314.3 Exception 1 & 2
Does the presence or absence of an EGC in the EMT affect your comments?So if EMT is used from the nonmetallic enclosure of the inverter to the nonmetallic deck-box, bonding (bushings) at both ends is required.
Well those plastic boxes are better than the boxes I expected when you said plastic. I agree: definitely place any plastic UNDER the panels.They don't have any pre-stamped knockouts, each one is drilled on site. Here are a couple of examples, one of which I think is pretty cool: