Im taking my journeymans exam in a couple of days and while studying I came across a question which has me stumped.
Which of the following is NOT considered a continuous load?
A. a stove
B. a flood light
C. a water heater
D. a fixed space heater
I answered a stove because most likely it would not be on for more than 3 hrs. at a time. Also the heating element doesn't continuously stay on while cooking.
A flood light would most likely be on all night. But based on what I am reading it says the answer is a flood light.
While studying I am finding a lot of info that is wrong. Could anyone please clarify this for me?
I would say the most likely answer is "A".
A flood light would be expected to be on for 3 or more hours on a regular basis. that is just the nature of such lights. You could create a scenario where it is not true, but the majority of the time most spotlights one would EXPECT to be on for 3 continuous hours or more.Continuous Load. A load where the maximum current is
expected to continue for 3 hours or more.
So most common water heaters will be continuous.422.13 Storage-Type Water Heaters. A fixed storage-type
water heater that has a capacity of 450 L (120 gal) or less shall
be considered a continuous load for the purposes of sizing
branch circuits.
Fixed electric space heaters are always continuous.424.3 (B) Branch-Circuit Sizing. Fixed electric space-heating
equipment and motors shall be considered continuous load
This is a good example of a poorly worded question.