kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
The fan itself would be "continuous" in that instance, but when it comes to heating effects and determination of branch circuit conductor ampacity - that fan is maybe only an amp of load but the heating element maybe is as low as 12 amps or as high as 20 amps on a typical household oven. When you size the conductor to handle the heater plus the fan - the ampacity is well covers the continuous portion of the load for this particular application.So maybe in a commercial/industrial application, a broiler might be considered a continuous load.
But for the run-of-the-mill residential application, I now understand how it isn't.
What about a convection oven, operating for 5 hours? Is the continuous fan a significantly smaller load than the thermostat cycling heat element?