Here's some OSHA Reg's, Texas does not have a State OSHA program that I saw listed.
You could get them on the GFCI that is not present but there is an out and not required if one follows all the below reg's of 1910.304(b)(3)(ii)(c).
You might be on the hook if you don't have a 1910.304(b)(3)(ii)(C)(1) PLAN...
I know the local's Inspectors would have a field day with the open cover.
I don't, nor have ever experienced anything like that on the job, it's more of
Label documentation that states "Danger - Hands Off", most trades will
show alot of but some no respect to usage and alot more self control than stated here in respects to temp. services provided.
I franklly can't believe some of the responses.
I can only hope this becomes a better understanding of while not stated in a working contract should be understood and practiced in the work place.
Standards numbers: (Taken from
Here)
Using the search of OSHA's page of "electrical standards." and isolatd it down to these wiring design and protection. This is just a particle listing.
1910.304(b)(3)(ii)
The following requirements apply to temporary wiring installations that are used during construction-like activities, including certain maintenance, remodeling, or repair activities, involving buildings, structures or equipment.
1910.304(b)(3)(ii)(A)
All 125-volt, single-phase, 15-, 20-, and 30-ampere receptacle outlets that are not part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit-interrupter protection for personnel.
Note 1 to paragraph (b)(3)(ii)(A) of this section: A cord connector on an extension cord set is considered to be a receptacle outlet if the cord set is used for temporary electric power.
Note 2 to paragraph (b)(3)(ii)(A) of this section: Cord sets and devices incorporating the required ground-fault circuit-interrupter that are connected to the receptacle closest to the source of power are acceptable forms of protection.
1910.304(b)(3)(ii)(B)
Receptacles other than 125 volt, single-phase, 15-, 20-, and 30-ampere receptacles that are not part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit-interrupter protection for personnel.
1910.304(b)(3)(ii)(C)
Where the ground-fault circuit-interrupter protection required by paragraph (b)(3)(ii)(B) of this section is not available for receptacles other than 125-volt, single-phase, 15-, 20-, and 30-ampere, the employer shall establish and implement an assured equipment grounding conductor program covering cord sets, receptacles that are not a part of the building or structure, and equipment connected by cord and plug that are available for use or used by employees on those receptacles. This program shall comply with the following requirements:
1910.304(b)(3)(ii)(C)(1)
A written description of the program, including the specific procedures adopted by the employer, shall be available at the jobsite for inspection and copying by the Assistant Secretary of Labor and any affected employee;
1910.304(b)(3)(ii)(C)(2)
The employer shall designate one or more competent persons to implement the program;