K8MHZ
Senior Member
- Occupation
- Electrician
"You Must, Unless" is still a variable.
The resistance to earth changes daily, that's why I think they should do away with the 25 ohms or less rule but that JMHO.
I agree with you 100 percent.
"You Must, Unless" is still a variable.
The resistance to earth changes daily, that's why I think they should do away with the 25 ohms or less rule but that JMHO.
Its based on the law of diminishing returns. Adding a second ground rod reduces the resistance by 60%, 3 gets a down to 40%, 3 is 30%.
Some one a long time ago determined that 2 was enough. This was all worked out probably by 1920. 6 feet apart is because closer than that the concentric shells of the earth overlap and it becomes one ground rod.
But 25 ohms? No one knows. Mike Holt emailed me once he thought he had the reason. But I don't think he ever found out for sure.
So....
Drive two and go home
Or
Use a concrete encased electrode.
Zog, you could but, it takes longer and is more expensive to test one rod than it is to drive a second rod and go home.Or....test it.
Its based on the law of diminishing returns. Adding a second ground rod reduces the resistance by 60%, 3 gets a down to 40%, 3 is 30%.
Some one a long time ago determined that 2 was enough. This was all worked out probably by 1920. 6 feet apart is because closer than that the concentric shells of the earth overlap and it becomes one ground rod.
But 25 ohms? No one knows. Mike Holt emailed me once he thought he had the reason. But I don't think he ever found out for sure.
So....
Drive two and go home
Or
Use a concrete encased electrode.
Don't get me wrong. I agree with installing grounding electrodes. I just think there should be 2 required and the clause about the "Unless 1 will do it" should be removed.
Where would the "Sphere of Influence" come into play here?
I lay one down and drive the second greater than the length apart. Don't care about 6', just the way I was taught...
Second rod is way cheaper than a test set.
Here is one reason from ECMweb: Why do I need to reach 25 ohms? The most credible answer to this question is: 25 ohms is a reasonable value to strive for, given the average soil resistivity for most regions of the United States.http://ecmweb.com/content/who-cares-about-25-ohms-or-less
Of course, he could have been guessing...
Zog, you could but, it takes longer and is more expensive to test one rod than it is to drive a second rod and go home.
Roger
25 ohms is a holdover from the land line telegraph era. That value was based upon the average expected distances from telegraph repeaters, whose structures housed the batteries for the systems. They used a SWER scheme for the system in order to conserve on wire. The sounders for the system could work on a wide range of voltages, but did have a minimum. Once distance between sounders, also commonly found at the repeater sites as few were not manned, caused enough voltage drop, voltage from the batteries were used to bump it up for the next trip. 25 ohms was a value determined to be a compromise between electrode installation costs and repeater construction costs.
"A reasonable value to strive for" is hardly a scientific answer. The real answer is simply that it was adopted from a technology no longer used and is archaic and meaningless for the electrical systems we work on.
I'm not doubting your reason, it sounds like the most logical. I don't know the exact reason, and only have these type publications to go on. I have wondered the reason for the 25 ohms for a couple of years. (along with so many others that guess)
Can you cite a source, so if I use that I don't have to say "cause K8MHZ said so"...
This might be a good topic for a poll, along these lines:
Having two grounds became necessary when:
(A) The ground rod mafia conned the code panel into helping them double their sales;
(B) Inspectors suddenly had attacks of 'the vapors' over the uncertainty of code language, even though 70 years of experience failed to identify any problems; or,
(C) Everyone suddenly decided electricians were but apes with tool belts, and needed every detail of their work determined by chairborne instant experts.
Renosteinke, check out the qualifications of the "chairborne instant experts". Their names and affiliations are in the front of the book. The guys I know on the code committees have worked decades in the trade and have probably forgotten more than you or I will ever know.
If he would have used the same type satire on the 25 ohm requirement I would have seen humor in it.
So here goes
The 25 ohm requirement became necessary when:
A) 1899 when the IBEW went on a national strike. The telegraph companies had figured out that they could use less wire (and less labor) by using the earth as a ground. Knowing that 25 ohms would not be easy and take additional materials and labor, they settled for that compromise in order to go back to work.
B) 1987 when cows started getting nervous and cross eyed.
C) 1906 when Henry Biddle was making a device that could measure electrode resistance and owned the NEC.
D) 1913 when several different values were tried, they were 16, 19 and 25. 25 won because it wouldn't be confused with the others if written upside down.
Using the "Fall of Potential Test." Here is one explanation, but you can Bing it yourself to get others.So, exactly how would you measure the resistance to earth?