Why are devices allowed to use the EGC as a current carrying conductor?

Status
Not open for further replies.

Tester101

Member
Location
New York
I was recently going to install a Lutron Maestro Occupancy Sensor (MS-OPS2), but I noticed in the installation instructions that it said the device wouldn't work without an equipment grounding conductor connected. This seemed strange to me, so I did a bit of research. I found that the device actually uses the grounding conductor as a grounded conductor, so it can have constant power. It only seems to be a small amount of current, as this document says you should be able to connect 20 devices before tripping a GFCI at 4-6mA.

But why is this allowed at all? Why are devices allowed to intentionally create ground faults? Shouldn't a normally non-current-carrying conductor, normally not carry current?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I was recently going to install a Lutron Maestro Occupancy Sensor (MS-OPS2), but I noticed in the installation instructions that it said the device wouldn't work without an equipment grounding conductor connected. This seemed strange to me, so I did a bit of research. I found that the device actually uses the grounding conductor as a grounded conductor, so it can have constant power. It only seems to be a small amount of current, as this document says you should be able to connect 20 devices before tripping a GFCI at 4-6mA.

But why is this allowed at all? Why are devices allowed to intentionally create ground faults? Shouldn't a normally non-current-carrying conductor, normally not carry current?
A normally non-current-carrying conductor should not be expected to carry normal current, regardless of how small. But at the same time there are designs that rely on it and have realllllllllly low current drain.
This a long story of conflict between the UL which approves the devices and NEC which essentially prohibits them. The partial resolution depends on the recent NEC provisions requiring a grounded conductor to be present (or easily pullable) at every box that contains a light switch.
 

cadpoint

Senior Member
Location
Durham, NC
A few plus years ago a Lutron "person" spoke/ posted on this exact subject. Maybe they can re-post their own article or the OP can research it.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I thought with the new code the use of the equipment grounding conductor would not be allowed. I have seen other manufacturers do the same - I started a thread on it. Here it is
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I thought with the new code the use of the equipment grounding conductor would not be allowed. I have seen other manufacturers do the same - I started a thread on it. Here it is
My impression is that with the changes made in NEC 2011 in effect, the current devices which use the EGC as a return path for control current will be grandfathered in their UL listing for some length of time (possibly forever) but no new lighting control or presence sensor devices will be approved by UL unless they use the neutral instead.
It is a chicken/egg thing and we are still in a transition.
If that impression is not correct, please give the right explanation. Thanks. :)
 

kwired

Electron manager
Location
NE Nebraska
My impression is that with the changes made in NEC 2011 in effect, the current devices which use the EGC as a return path for control current will be grandfathered in their UL listing for some length of time (possibly forever) but no new lighting control or presence sensor devices will be approved by UL unless they use the neutral instead.
It is a chicken/egg thing and we are still in a transition.
If that impression is not correct, please give the right explanation. Thanks. :)
That is kind of my thoughts. They probably stop making them rely on the EGC as part of the circuit at some point if they want them to have a valid listing, but I don't know when that point is.
 